IR Flame Detectors
-
- I have made <0 posts
- Posts: 7
- Joined: Thu Oct 01, 2015 12:48 am
- 7
- Full Name: Paul Donnelly
- Company Details: 4Z Pty Ltd
- Company Position Title: 4Z Pty Ltd
- Country: Australia
- Linkedin Profile: Yes
- Been thanked: 1 time
IR Flame Detectors
Hi all,
I am on an oil and gas facility and the question has been raised about whether my P40 laser scanner will affect or trigger the IR flame detectors in the area.
Through my experience it is extremely unlikely (impossible?) that the detectors can be set off by our scanner, but i would like to show evidence of that. My understanding is that the wavelength emitted by the P40 is too large to affect the flame detector sensors.
Can anyone provide any further info on this?
Many thanks,
Paul
I am on an oil and gas facility and the question has been raised about whether my P40 laser scanner will affect or trigger the IR flame detectors in the area.
Through my experience it is extremely unlikely (impossible?) that the detectors can be set off by our scanner, but i would like to show evidence of that. My understanding is that the wavelength emitted by the P40 is too large to affect the flame detector sensors.
Can anyone provide any further info on this?
Many thanks,
Paul
- Matt Young
- Global Moderator
- Posts: 3929
- Joined: Fri Nov 30, 2007 3:03 pm
- 15
- Full Name: Matt Young
- Company Details: Baker Hicks
- Company Position Title: CAD-BIM Lead
- Country: UK
- Linkedin Profile: No
- Has thanked: 45 times
- Been thanked: 40 times
Re: IR Flame Detectors
I have tested these flame detectors in the past with a scanner right in front of them. This was in a lab conditions, in three different labs around the world. Nothing happened at all.
If you don't see that there is nothing, then you are kidding yourself.
-
- I have made <0 posts
- Posts: 9
- Joined: Thu Jan 31, 2019 4:51 am
- 4
- Full Name: Eric Winkelman
- Company Details: FERASCO [forensic evidence]
- Company Position Title: Partner
- Country: United States
- Linkedin Profile: No
Re: IR Flame Detectors
Short answer no.
Those detectors are tuned to detect water vapor or CO2 IR absorbance wavelength. Along with and/or UV. About 0.2 um, 3.5 um, and 4.3 um wavelength. And sometimes combined with visual detection. P40 datasheet states 1,550 nm [1.55 um]. They need to see sustained patterns or durations as well to avoid false detection. Beside all of that I would think that the flame detectors cannot respond fast enough to a pulse from the scanner.
Those detectors are tuned to detect water vapor or CO2 IR absorbance wavelength. Along with and/or UV. About 0.2 um, 3.5 um, and 4.3 um wavelength. And sometimes combined with visual detection. P40 datasheet states 1,550 nm [1.55 um]. They need to see sustained patterns or durations as well to avoid false detection. Beside all of that I would think that the flame detectors cannot respond fast enough to a pulse from the scanner.
-
- I have made <0 posts
- Posts: 7
- Joined: Thu Oct 01, 2015 12:48 am
- 7
- Full Name: Paul Donnelly
- Company Details: 4Z Pty Ltd
- Company Position Title: 4Z Pty Ltd
- Country: Australia
- Linkedin Profile: Yes
- Been thanked: 1 time
Re: IR Flame Detectors
Thanks very much for the input guys.
At the clients insistence we ended up running a test scan directly in front of an inhibited sensor and unsurprisingly it had no affect.
Paul
At the clients insistence we ended up running a test scan directly in front of an inhibited sensor and unsurprisingly it had no affect.
Paul
- Matt Young
- Global Moderator
- Posts: 3929
- Joined: Fri Nov 30, 2007 3:03 pm
- 15
- Full Name: Matt Young
- Company Details: Baker Hicks
- Company Position Title: CAD-BIM Lead
- Country: UK
- Linkedin Profile: No
- Has thanked: 45 times
- Been thanked: 40 times
Re: IR Flame Detectors
Good that you ran the test. It's always best to be safe. And now your client has a little extra confidence in what you are doing for them 

If you don't see that there is nothing, then you are kidding yourself.
-
- I have made 100> posts
- Posts: 108
- Joined: Thu Mar 09, 2017 4:27 pm
- 6
- Full Name: Gordon
- Company Details: Roskda DBO
- Company Position Title: GIS Coordinator
- Country: Canada
- Linkedin Profile: Yes
- Location: Alberta
- Has thanked: 9 times
- Been thanked: 11 times
Re: IR Flame Detectors
We scanned a gas plant last week that had an emergency shutdown. Alarm went off, flare stack was burning all sorts of stuff, shooting green flame 60 odd feet in the air. Plant was down for about an hour before they started bringing it back online again. All hands on deck. All of that was caused by a welder in one of the buildings, who set off a fire-eye. The operators were supposed to bypass it, but must have forgotten.
I've never set one off, and we use x330's and RTC360's. I as well, checked the wavelengths as mentioned by Eric prior to scanning, but it makes me sweat a bit every time I see one.
I've never set one off, and we use x330's and RTC360's. I as well, checked the wavelengths as mentioned by Eric prior to scanning, but it makes me sweat a bit every time I see one.
- Matt Young
- Global Moderator
- Posts: 3929
- Joined: Fri Nov 30, 2007 3:03 pm
- 15
- Full Name: Matt Young
- Company Details: Baker Hicks
- Company Position Title: CAD-BIM Lead
- Country: UK
- Linkedin Profile: No
- Has thanked: 45 times
- Been thanked: 40 times
Re: IR Flame Detectors
I have seen the damage done when the shut down doesn't work. It's nice to know that one didgordonired wrote: ↑Mon Oct 28, 2019 5:45 pm We scanned a gas plant last week that had an emergency shutdown. Alarm went off, flare stack was burning all sorts of stuff, shooting green flame 60 odd feet in the air. Plant was down for about an hour before they started bringing it back online again. All hands on deck. All of that was caused by a welder in one of the buildings, who set off a fire-eye. The operators were supposed to bypass it, but must have forgotten.
I've never set one off, and we use x330's and RTC360's. I as well, checked the wavelengths as mentioned by Eric prior to scanning, but it makes me sweat a bit every time I see one.

If you don't see that there is nothing, then you are kidding yourself.
- DelioPontes
- V.I.P Member
- Posts: 213
- Joined: Fri Dec 14, 2007 1:45 pm
- 15
- Full Name: Delio Pontes
- Company Details: Fugro
- Company Position Title: Engineering Surveyor
- Country: United Kingdom
- Linkedin Profile: Yes
- Location: United Kingdom
- Contact:
Re: IR Flame Detectors
I had the same issue in my last job with a total station on an Oil Rig, even trying to explain to them the platform was fully covered with B&W targets from an old job done by another company...For decades Total Stations and Laser Scanners equipment has been used in this environment with no issues... and we point the total station to targets, not Fire/Gas alarms...
Does anyone have any documentation of the IR or the laser beam? cannot trig the alarms?
Does anyone have any documentation of the IR or the laser beam? cannot trig the alarms?
- TommyMaddox
- V.I.P Member
- Posts: 490
- Joined: Mon Apr 25, 2016 7:15 pm
- 6
- Full Name: Tommy R Maddox III
- Company Details: ONSITE3D
- Company Position Title: Director of Technology
- Country: USA
- Linkedin Profile: Yes
- Location: Calgary, Alberta
- Has thanked: 52 times
- Been thanked: 114 times
Re: IR Flame Detectors
We always request hot work permits to cover our bases and address the non intrinsically safe behavior of the units. It also allows us to run electric drills on site for permanent reference installation. Getting the fire eyes bypassed is not an issue and we've done ~1000 oil and gas sites.